"Gen sys tmpr" in DSC 1864 ans 5108 extension module
« on: November 27, 2007, 01:32:50 AM »
Hi

I've a problem with 5108 extension module.
When I connect it with DSC 1864 by keybus I'm getting "gen sys tmpr" system trouble.
I've no idea what is the problem - could you help me?.

Thanks for help

__
jazz

rahnie

  • Security Guru
  • ****
  • Posts: 1293
  • Karma: +0/-0
  • i know nothing and i can prove it
    • View Profile
Re: "Gen sys tmpr" in DSC 1864 ans 5108 extension module
« Reply #1 on: November 27, 2007, 01:50:48 AM »
on the expansion module, jumper the tamper terminal to aux - or C of one of the zones.........cheers
« Last Edit: November 27, 2007, 01:52:30 AM by rahnie »
The trick of thinking outside of the box is knowing when to get back in
The original point and click interface was a Smith & Wesson

jazz

  • Member
  • *
  • Posts: 6
  • Karma: +0/-0
    • View Profile
Re: "Gen sys tmpr" in DSC 1864 ans 5108 extension module
« Reply #2 on: November 27, 2007, 02:15:15 AM »
thanks for very fast reply :)
I'll check it this evening

__
jazz

rahnie

  • Security Guru
  • ****
  • Posts: 1293
  • Karma: +0/-0
  • i know nothing and i can prove it
    • View Profile
Re: "Gen sys tmpr" in DSC 1864 ans 5108 extension module
« Reply #3 on: November 27, 2007, 06:13:42 AM »
not sure where you are at with the module, so i'll mention that there are jumpers to be set on the module to define which zones the module is to supply......after setting those to suit and installing that tamper jumper you'll want to enter programming and enter 902 to enroll the module to the system....wait a coupla minutes and exit programming (you can enter 903 first to view enrolled modules and the zones set by the on board jumpers).....if the module is already enrolled with zones to suit, all you should have to do is the tamper jumper to clear the trouble....cheers
The trick of thinking outside of the box is knowing when to get back in
The original point and click interface was a Smith & Wesson

jazz

  • Member
  • *
  • Posts: 6
  • Karma: +0/-0
    • View Profile
Re: "Gen sys tmpr" in DSC 1864 ans 5108 extension module
« Reply #4 on: November 27, 2007, 01:02:00 PM »
thank You very much
it works now :)